IMPORTANT!!!
Surely
connect the frame of the KX-Tl23210
to earth
ground
properly
to protect the unit.
4
To earth ground
In most continental
united states, the ground provided
by the " third wire ground" at the commercial
power outlet
will be satisfactory
however,
in a small percentage
this ground
may be installed
in correctly.
Therefore,
the following
test procedure
should
be performed.
Test Procedure
1.
2.
3.
4.
5.
Obtain
a suitable
voltmeter
and set it for a possible
reading
of up to 250 VAC
Connect
the meter probes
between
the two main AC voltage
points on the wall outlet. The reading
obtained
should
be 108-132
VAC.
Move one of the meter probes to the 3rd prong terminal
(GND).
Either the same reading
or a reading
of 0 volt should
be obtained.
If a reading of 0 volt at one terminal
and a reading of 108-l 32 VAC at the other terminal
is not obtained,
the
outlet is not properly
grounded.
This condition
should
be corrected
by a qualified
electrician
(per article 250 of the National
Electrical
Code).
If a reading of 0 volt at one terminal
and a reading of 108-l 32 VAC at the other terminal
is obtained,
then set
the meter to the " OHMS/RX1
" scale, place one probe at the GND Terminal
and the other probe at the terminal
which
gave a reading
of 0 volt.
A reading
of less than 1 ohm should
be obtained.
If the reading
is not obtained
the outlet
is not adequately
grounded,
see qualified
electrician.
2-2