6. Press up ! or down " until the desired
temperature is displayed.
7. Press Not Occupied Cool.
8. Press up ! or down " until the desired
temperature is displayed.
9. Press Run Schedule.

Temperature Setpoint Overrides

IMPORTANT
— Setup determines Occupied override
duration.
— Default duration is three hours.
NOTE: To cancel Override and immediately
return to the program, press Run
Schedule.
T7770 Setpoint Knob
A T7770 setpoint knob can remotely adjust the
T7350 setpoint. This adjustment can be made
when the sensor is in override.
NOTES:
During override, only occupied and
standby heat setpoints, and cool
setpoints are adjusted.
The maximum adjustment is ±5 °F
(±3 °C).
With a disconnected or failed
T7770, or a T7350 set for local
temperature sensing, offset is zero.
Using Temporary Occupied Override
The Temporary Occupied Override can be used
when the T7350 is in Not Occupied or Standby
mode. It switches to the Occupied mode for a
fixed number of hours.