1. To use the default occupied override,
press Temporary Occupied.
NOTE: The default temperature setting
is the Occupied setpoint.
2. To select a temperature setting other than
the default, press up ! or down " until
desired temperature offset displays
(range is configurable by the installer
from 0 to 5 °F (0 to 3 °C)).
Using Temporary Not Occupied Override
The Temporary Not Occupied Override fixes the
device to operate in Not Occupied mode for a
number of days (between 1 and 99) without
changing the programming saved in memory.
NOTES:
If the number of days is set to zero,
no temporary change takes effect.
If the number of days is set just
below zero, the display for days is
"---" (an indefinite override).
To turn off this override, you must
press Run Schedule.
1. Press Temporary Not Occupied.
2. Press up ! or down " to change the
duration of the Not Occupied period (in
days).
NOTE: The default temperature setting
is the Not Occupied setpoint.
3. Press
11
to display the default setpoint.
63-2652