GENERAL
The TP9600 Series pneumatic thermostat provides
proportional control for pneumatic actuators in heating,
ventilating, and air conditioning systems.
FEATURES
• One, two, or three pipe
• Direct Acting and Reverse Acting
• One or two bimetal elements for Day-Night or
Heating-Cooling operation
• High capacity or one pipe low capacity devices
• Adjustable stops to limit setpoint adjustment
• Replaceable Air Filter
• Includes cover
Copyright © 1996 Honeywell Inc. • All Rights Reserved
TP9600-TP9630 Pneumatic
SPECIFICATIONS
Air Pressure:
25 psi max
18 psi operating
Setpoint Pressure:
Factory set at 8 psi
Air Consumption:
0.011 scfm
Setpoint Range:
60 to 90 F typical
50 to 75 F setback
Throttling Range:
2 to 10 F, Factory set at 4 F
Air Connections:
5/32 barb fittings
Branch Line Port:
Self-Sealing tap accessible under cover
Maximum Ambient Temperature:
150 F
Mounting:
Vertical wall mount with plug in backplate
ACCESSORIES
14002430-001: Protective Guard, Standard
TG509F,G: Protective Versaguard, Key Lock
14004439-001: Setpoint Extension Lever
Common Repair Parts
14001865-001: Filter Cartridge Assembly
Kits
14004911-001: Adaptor Plate Assembly
This kit adapts the TP9600 to replace newer
Johnson, Powers, Robertshaw, and Kreuter
thermostats
14002573-001: Universal Modernization Kit
This kit adapts the TP9600 to replace older
Honeywell and other manufactures of larger
thermostats
Thermostats
INSTALLATION INSTRUCTIONS
95-7550