Distance between front and rear mounting planes between 24 to 36 inches
(650 mm and 915 mm).
Minimum clearance depth (to front cabinet door) in front of front rackmount
plane: 1 inch (25.4 mm).
Minimum clearance depth (to rear cabinet door) behind front rackmount plane:
31.5 inches (800 mm) with cable management arm (recommended) or 27.5 inches
(700 mm) without the cable management arm.
Minimum clearance width (between structural supports and cable troughs)
between front and rear mounting planes: 18 inches (456 mm).
Note – Two-post racks are not compatible.
Related Information
SPARC Enterprise T5440 Server Site Planning Guide
"Tools and Equipment Needed" on page 2
"Cabling Notes" on page 5
"About the Slide Rail Assembly" on page 7
"About the Cable Management Arm" on page 8
"Installing the SPARC Enterprise T5440 Server" on page 13

Safety Precautions

Caution – Deploy the antitilt bar on the equipment rack before beginning an
installation.
Caution – Always load equipment into a rack from the bottom up so that it will not
become top-heavy and tip over.
Caution – The SPARC Enterprise T5440 server weighs approximately 88 lb. (40 kg).
Two people are required to lift and mount this server into a rack enclosure when
using the procedures in this document.
10
SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009