Temperature Setpoints; Setpoint Limits - Honeywell T7350 Features

For conventional/heat pump systems
Hide thumbs Also See for T7350:
Table of Contents

Advertisement

Clearing Program Start Times
1. Press Occupied or Not Occupied until the
start period to be cleared is displayed.
2. Press Day until desired day is displayed.
3. Press Clear Start Time.
4. Repeat steps 1 through 3 for all the start
times to be cleared.
5. Press Run Schedule.

Temperature Setpoints

Setpoint Limits

The setpoint temperature range is 40°F to 90°F
(4°C to 32°C) for heating and 45°F to 99°F
(7°C to 37°C) for cooling.
NOTES: The ranges mentioned can be limited
based upon setpoints and stops:
1.
The greater of the Minimum Heat
Stop and the Not Occupied Heat set-
points determines the lowest setting
to which the occupied heat setpoint
can be adjusted: Stop/NotOcc
OccHeat
2.
The lesser of Maximum Cool Stop
and Not Occupied Cool setpoints
determines the highest setting to
which the occupied cool setpoint can
be adjusted: Stop/NotOcc OccCool
(OccHeat + 2).
3.
The Maximum Occupied Heat Set-
point is limited by Occupied Cool
Setpoint – 2.
4.
The Minimum Occupied Cool Set-
point is limited by the Occupied Heat
Setpoint + 2.
9
(OccCool - 2).
63-2604