Venstar T2800 Installation Instructions Manual

Venstar T2800 Installation Instructions Manual

Commercial 7-day programmable up to 3-heat & 2-cool
Hide thumbs Also See for T2800:

Advertisement

Digital
Digital
Thermostat
Thermostat
Control up to 3 Heat &
2 Cool Stages
3 Configurable Outputs
Adjustable 2nd & 3rd Stage
Timers & Deadbands
Backlit Display & Button
Legends
Aux Heat Indicator
Set Point Limiting
Meets Commercial California Title 24
Use with most Air Conditioning & Heating Systems including: 1 or 2 Stage
Electric Cooling & 3 Stage Gas Heating, Heat Pump, Electric or Hydronic Heat.
INSTALLATION
INSTALLATION
INSTRUCTIONS
INSTRUCTIONS
Venstar Inc. 08/07
commercial
THERMOSTAT
T2800
7-DAY
7-DAY
PROGRAMMABLE
PROGRAMMABLE
up to 3-heat
up to 3-heat
& 2-cool
& 2-cool
HEAT
HEAT
COOL
PUMP
Outdoor Sensor Ready with
High/Low Readouts for the Day
Accepts EZ Programmer
Accepts Optional Humidity
Module: Controls Humidification
and Dehumidification
Accepts Optional IR
Remote Control
Accepts Comfort Call
Phone Control Accessory

Advertisement

loading
Need help?

Need help?

Do you have a question about the T2800 and is the answer not in the manual?

Questions and answers

Teri Peoples
March 5, 2025

VenStar T2800 Red Light on - furnace not running

User image 67c8de83d94db

Summary of Contents for Venstar T2800

  • Page 1 Phone Control Accessory Meets Commercial California Title 24 Use with most Air Conditioning & Heating Systems including: 1 or 2 Stage Electric Cooling & 3 Stage Gas Heating, Heat Pump, Electric or Hydronic Heat. INSTALLATION INSTALLATION INSTRUCTIONS INSTRUCTIONS Venstar Inc. 08/07...
  • Page 2 (1) this device may not cause harmful interference, and (2) this device must accept any interference received, including interference that may cause undesired operation. Thermostat T2800 Tested to Comply with FCC Standards FOR HOME OR OFFICE USE...
  • Page 4: Table Of Contents

    Table of Contents Preparation Remove & Replace the Old Thermostat Configuring the MISC Outputs Wire Connections Sample Wiring Diagrams Test Operation Calibrating the Thermostat Sensors TroubleShooting Page...
  • Page 5: Preparation

    SECTION 1 Preparation Proper installation of the thermostat will be I2:00 accomplished by following these step by step AUTO instructions. If you are unsure about any of these steps, call a qualified technician for assistance. Assemble tools I2:00 AUTO Flat Blade Wire cutter Screwdriver &...
  • Page 6: Remove & Replace The Old Thermostat

    SECTION 2 Remove & Replace the Old Thermostat Remove the cover of the old thermostat. I2:00 AUTO If it does not come off easily check for screws. Loosen the screws holding the thermostat I2:00 AUTO base or subbase to the wall, and lift away. Disconnect the wires from the old thermostat.
  • Page 7: Configuring The Misc Outputs

    SECTION 3 Configuring the MISC Outputs Section 3 Contents: Configuring the Jumpers..3.2 Explanation of Jumper Settings........3.3 Page 3.1...
  • Page 8 Configuring the Jumpers For additional flexibility, your thermostat has three configurable outputs. These outputs are designed to have different functions depending on how the jumpers are set (below). Each output, labeled MISC1, MISC2, and MISC3 may be set for one of the four choices available.
  • Page 9 Explanation of Jumper Settings W3 JUMPER SETTING If the jumper for MISC1, MISC2, or MISC3 is set to W3, the corresponding MISC screw terminal on the backplate will control a third stage of heat. W3 MULTI-STAGE OPERATION EXPLAINED - SECTION 13 of the Owner’s Manual The 3rd Stage of Heat is turned on when: (A) The 1st and 2nd stages have been on for the time required (steps 23...
  • Page 10 Explanation of Jumper Settings (continued) DEHUM JUMPER SETTING If the jumper for MISC1, MISC2, or MISC3 is set to DEHUM, the corresponding MISC screw terminal on the backplate will be connected to the dehumidification terminal of a furnace board. NOTE: Not all furnaces have a dehumidification terminal. DEHUMIDIFICATION OPERATION - SECTION 10 of the Owner’s Manual If your HVAC unit is equipped with a dehumidification system the thermostat will operate in one of two ways.
  • Page 11 Explanation of Jumper Settings (continued) Y2 JUMPER SETTING If the jumper for MISC1 is set to Y2 the MISC1 screw terminal on the backplate will control a second stage of cooling. Y2 OPERATION - SECTION 13 of the Owner’s Manual Control up to two Cool stages.
  • Page 12: Wire Connections

    SECTION 4 Wire Connections If the terminal designations on your old thermostat I2:00 AUTO do not match those on the new thermostat, refer to the chart below, or the wiring diagrams that follow. Wire from the Install on the new thermostat old thermostat Function connector marked...
  • Page 13: Sample Wiring Diagrams

    SECTION 5 Sample Wiring Diagrams Section 5 Contents: HVAC Equipment Wiring....5.2 MISC1, MISC2, and MISC3 Wiring........5.6 Installing the Outdoor Sensor...5.8 Page 5.1...
  • Page 14 6 Wire, 1 Stage Cooling, 1 Stage Heat Residential & Commercial 1 Stage Cooling, Commercial Heat Pump 1 Stage Cooling with 1st Stage Gas Heat with 2 Stage Heat W1/O/B MISC1 MISC3 MISC2 RS+5 RSGND ELEC 6 Conductor 18 gauge ELEC unshielded cable from the DEHUM...
  • Page 15 6 Wire, 1 Stage Cooling, 1 Stage Heat Residential & Commercial 1 Stage Cooling, with 1st Stage Electric Heat W1/O/B MISC1 MISC3 MISC2 RS+5 RSGND ELEC 6 Conductor 18 gauge ELEC unshielded cable from the DEHUM thermostat to the equipment. (MISC1 MISC3 MISC2...
  • Page 16 6 Wire, 1 Stage Cooling, 2 Stage Heat Residential Heat Pump with O Reversing Valve 1 Stage Cooling, with 2 Stage Heat W1/O/B MISC1 MISC3 MISC2 RS+5 RSGND ELEC 6 Conductor 18 gauge ELEC unshielded cable from the DEHUM thermostat to the equipment. (MISC1 MISC3 MISC2...
  • Page 17 6 Wire, 1 Stage Cooling, 2 Stage Heat Residential Heat Pump with b Reversing Valve 1 Stage Cooling, with 2 Stage Heat W1/O/B MISC1 MISC3 MISC2 RS+5 RSGND ELEC 6 Conductor 18 gauge ELEC unshielded cable from the DEHUM thermostat to the equipment. (MISC1 MISC3 MISC2...
  • Page 18 Adding a 2nd Stage of Cooling (MISC1) and a 3rd Stage of Heating (MISC3) W1/O/B MISC1 MISC3 MISC2 RS+5 RSGND ELEC DEHUM (MISC1 MISC3 MISC2 MISC1 ONLY) MISC1 MISC2 MISC3 DEHUM RS+5 INSTALL HUMIDITY MODULE WITH SENSING RSGND ELEMENT OUTWARD (MISC1 MISC3 MISC2...
  • Page 19 Adding a Humidification System (MISC1) and Dehumidification System (MISC2) W1/O/B MISC1 MISC3 MISC2 RS+5 RSGND ELEC PROG NO HUM DEHUM (MISC1 MISC3 MISC2 MISC1 ONLY) MISC1 MISC2 MISC3 DEHUM RS+5 INSTALL HUMIDITY MODULE WITH SENSING RSGND ELEMENT OUTWARD Humidity Module (MISC1 (Sold Separately) MISC3...
  • Page 20 Installing the Outdoor Sensor The Outdoor Sensor measures outdoor air temperature and sends this information to the thermostat; it measures temperature with a range of -40 to 127 F. The Outdoor Sensor should be connected to the thermostat using solid conductor CAT 5, CAT 5e, or CAT 6 type network commun- ication cable.
  • Page 21: Test Operation

    SECTION 6 Test Operation Turn the power on to the Heating/Air Conditioning I2:00 AUTO system. Press the MODE button repeatedly until the I2:00 AUTO HEAT icon appears on the display. Press UP or DOWN buttons until the set temperature is 10 degrees above room temperature; the furnace should turn on.
  • Page 22: Calibrating The Thermostat Sensors

    SECTION 7 Calibrating the Thermostat Sensors Under normal circumstances it will not be necessary to adjust the calibration of the temperature and humidity sensors. If calibration is required, please contact a trained HVAC technician to correctly perform the following procedure. I2:00 Place the thermostat in the MODE...
  • Page 23: Troubleshooting

    SECTION 8 TroubleShooting SYMPTOM: The air conditioning does not attempt to I2:00 turn on. AUTO CAUSE: The compressor timer lockout may prevent the air conditioner from turning on, for a period of time. REMEDY: Consult the Owner's Manual in the Setup section to defeat the cycles per hour and compressor timeguard.
  • Page 24 TroubleShooting SYMPTOM: When controlling a residential heat pump, I2:00 AUTO and asking for cooling, the heat comes on. CAUSE: The thermostat reversing valve jumper is set for “b”. REMEDY: Set the reversing valve jumper for “O”. See pages 5.4 and 5.5. SYMPTOM: When calling for cooling, both the heat I2:00 AUTO...