Honeywell T7351 Installation Instructions Manual page 5

Commercial programmable thermostat for single- or multi-stage conventional/heat pump systems
Hide thumbs Also See for T7351:
Table of Contents

Advertisement

Text
Default
DEGREES 0
0 -1
CLOCK
0
0 - 1
KEYLOCK 0
0 - 3
HEATPMP 0
0 - 2
COOLSTG 1
0 - 4
HEATSTG 1
0 - 3
AUX STG
0
0 - 2
AUX CON
0
0 - 3
WALLMOD 0
0 - 3
OATSENS 0
0 - 1
DATSENS 0
0 - 1
HUMSENS 0
0 - 2
OCCSENS 0
0 - 1
FAN HT
0
0 - 1
Table 3. Installer Setup.
Choices
Degree Temperature Format
0: Degrees F
1: Degrees C
Clock Display Format
0: 12 hour
1: 24 hour
Keypad Lockout Level
0: None
1: Lockout all keys except Set Day, Set Time, Set Date, Set Holidays,
Temporary Occupied, Temporary Not Occupied, System, Fan, Up, Down and
Information
2: Lockout all keys except Set Day, Set Time. Set Date, Set Holidays,
Temporary Occupied, Temporary Not Occupied, Up, Down and Information
3: Lockout all keys except Information
Application Type Selection
0: Conventional
1: Heat Pump - Cooling (Energize O/B on call for cool)
2: Heat Pump - Heating (Energize O/B on call for heat)
Number of Cooling Stages
0: 0 Stages of Cooling
1: 1 Stages of Cooling
2: 2 Stages of Cooling
3: 3 Stages of Cooling
4: 4 Stages of Cooling (W3 will be used as 4th stage relay)
Number of Heating Stages
0: 0 Stages of Heating
1: 1 Stages of Heating
2: 2 Stages of Heating (This is the max if 4 cooling stages is selected)
3: 3 Stages of Heating
Only shown when Heat Pump is selected
0: 0 Aux Stages
1: 1 Aux Stages
2: 2 Aux Stages
Aux Contact Functionality
0: Time of Day
1: Economizer
2: Dehumid - Hot Gas Bypass
3: Simple Dehumid
Remote Room Sensor Selection
0: Local sensor only
1: T7770A/D (Remote Sensor, No Remote Setpoint, Bypass 0)
2: T7770B/C (Remote Sensor, Remote Setpoint, Bypass 0)
3: T7771 (Remote sensor, Remote Setpoint, Bypass 1)
(Display only if sub-base 2, 3, 4+)
(This item is not displayed when
Outdoor Air Sensor Selection
0: None
1: Remote Outdoor Air Sensor
Discharge Air Sensor Selection
0: None
1: Remote Discharge Air Sensor
Room Humidity Sensor selection
0: None
1: On Board Sensor
2: Remote Sensor
Occupancy Sensor Selection
0: None
1: Remote Occ Sensor
Fan Operation on Heat
0: Conventional (Equipment controls Fan)
1: Electric (Thermostat turns on Fan with call for Heat)
T7351 COMMERCIAL PROGRAMMABLE THERMOSTAT
Notes
5
62-0258