Installer System Test - Honeywell T8501 Installation Instructions Manual

Microelectronic thermostats
Hide thumbs Also See for T8501:
Table of Contents

Advertisement

INSTALLER SYSTEM TEST

Use the Installer System Test to check the thermostat
operation. Refer to Table 3 for a list of the available
system tests.
CAUTION
Equipment Damage Hazard.
Minimum off time for compressor is bypassed
during Installer System Test.
Prevent compressor from cycling too quickly.
To start the system test:
Press and hold the increase ! and decrease # keys at
the same time until two zeros (00) appear. All segments
of the LCD are displayed before 00 appears.
See Fig. 11 and 12.
Table 3. Tests Available In Installer System Test.
Test
Number
System Test Description
10-19
Heating equipment can be turned on and
off.
30-39
Cooling equipment can be turned on and
off.
40-49
Fan equipment can be turned on and off.
60 0 to
Keyboard keys test.
60 19
70-79
Thermostat information including date
code and software versions are displayed.
Keys to
Test
Press
Number
Heating Equipment System-Test
i
10
Enter heating equipment system-test. (Set System switch to Heat on switch models.)
11
Heat comes on. When Installer Setup number 02 is 01, the system fan is also energized.
!
10
Heat and system fan turn off.
#
Cooling Equipment System Test
i
30
Change from heating to cooling equipment system test. (Set system switch to Cool on
switch models.)
31
Cool and system fan come on.
!
30
Cool and system fan turn off.
#
Fan Equipment System Test (T8501D only)
i
40
Change from cooling to fan equipment system-test.
41
Fan comes on.
!
40
Fan turns off.
#
Em Ht Temporary Setting
Aux Ht
Repl
Batt
System
Em HeatOffCool Auto Only
Fig. 12. Display of all LCD segments.
Refer to Table 4 for the directions and results of the
specific tests.
IMPORTANT
Models with System and Fan switches must set
the switches to the equipment that is being
checked for the equipment to operate.
NOTE: Press and hold the increase ! and decrease #
keys for three seconds to exit the system test
mode. The system test times out after five min-
utes without any key presses.
Table 4. Installer System-Test Options.
Description
7
T8501 MICROELECTRONIC THERMOSTATS
Remote
%Humid
Outdoor
Wait
Heat Cool
OnAuto
TEST NUMBER
Fig. 13. Display of test number.
Room
Fan
M4844
M6792A
69-0925—4