Set Thermostat Dip Switches - Honeywell T7200 Manual

Programmable commercial thermostats and subbases
Hide thumbs Also See for T7200:
Table of Contents

Advertisement

Standard
Alternate
Terminal
Designations Or
Designation
Customer Specials
B
E
K
G
F
O
R
R
V
RC
RH
W1
H1, R3
W2
H2, Y, R4
W3
Y1
C1, M
Y2
C2
a
Y3
X
X1,X2,C
T
L, C, H
O
LED1,
A,A1,A2,Z,C,L
LED2, COM
T
R1, R2
RS
Y
M
A1, A2, A3
CA1-CA5
a
Q7300G only.
b
Shielded cable can be required in some installations where electrical interference (noise) can cause control problems.

SET THERMOSTAT DIP SWITCHES

The thermostat DIP switches provide the thermostat
with an interface to the single zone HVAC system. See
Table 7 for DIP switch settings. The thermostat DIP switches
are located on the back of the thermostat. See Fig. 13. Set
the DIP switches for the desired thermostat features and the
system being controlled.
IMPORTANT: The thermostat configuration must match
the application, or the control logic will not function
properly.
TABLE 6—TERMINAL DESIGNATIONS.
Typical Connection
Heating damper motor; changeover valve/relay
Emergency heat relay
Fan relay coil
Cooling damper motor; changeover valve/relay
Power connection to transformer (internally
connected for heating and cooling)
Power connection to cooling transformer
Power connection to heating transformer
Stage 1 heating control
Stage 2 heating control
Stage 3 heating control
Stage 1 cooling control
Stage 2 cooling control
a
Stage 3 cooling control
Common connection
b
Remote sensor
HSII control panel
Momentary circuit, changeover
LEDs
External temperature readout, T relay
LO and HI speed fan relays
Cooling contactor
Compressor contactor
Auxiliary relay
b
Remote override
9
Function
Output
Output
Output
Output
Input
Input
Input
Output
Output
Output
Output
Output
Output
Input
Input
Annunciation
Output
Input
TABLE 7—THERMOSTAT DIP SWITCH SETTINGS
Switch Setting
°F display
a
1
ON
°C display
OFF
a
2
ON
12 hour clock display
OFF
24 hour clock display
a,b
3
ON
Intermittent fan operation in occupied
period
OFF
Continuous fan operation in occupied
period
4
Nonfunctional switch
a
5
ON
Keyboard is used for programming
OFF
Keyboard disabled, but can be used to
review program, perform overrides
and make clock changes.
a
Factory setting.
b
Q7300B,C,D,E,L: fan switch will override this switch
setting.
Q7300A,F,G: no override is available.
T7200/T7300/Q7300
INSTALLATION
Terminal Type
24 Vac powered contact
24 Vac powered contact
24 Vac powered contact
24 Vac powered contact
24 Vac powered contact
24 Vac powered contact
24 Vac powered contact
24 Vac powered contact
24 Vac powered contact
24 Vac powered contact
Dry contact
Low power
Function
63-4038—7

Advertisement

Table of Contents
loading

This manual is also suitable for:

T7300Q7300

Table of Contents